7/6/2012 11:23 PM | |
Posts: 2 Rating: (0) |
Hello All, I have configured the screen in logo TD to appear the Flag status in case of on/off. When I run the simulation every thing was OK, but when I transferred the program to PLC & Logo TD, the Falg status didn't appear. Can you help me in this issue, I don't know why the difference between the simulation and the actual case in display. Regards,
AttachmentCircuit Diagram2.zip (217 Downloads) |
7/9/2012 8:09 AM | |
Posts: 153 Rating: (17) |
Hi,LOGO_Ferass. Keys f1-f4 LOGO TD work in a momentary pushbutton mode in the actual case in display. It is required to establish the additional block "pulse relay". AttachmentCircuit Diagram2.zip (216 Downloads) |