4/19/2016 4:32 PM | |
Posts: 112 Rating:
|
hardware configuration: |
4/19/2016 4:34 PM | |
Posts: 112 Rating:
|
Hope you could see what causes the problem, I suspect the AI block. Diagnostic buffer log is included.AttachmentDiagnoseSiemens.txt (252 Downloads) |
Last edited by: AGrS at: 4/19/2016 4:35:02 PM |
|
4/19/2016 6:02 PM | |
Joined: 9/7/2007 Last visit: 10/9/2024 Posts: 550 Rating:
|
Hi AGrS Is this error related to any process action? is there any frequency convertor near to the communication cable? Are you in a commissioning phase? or it is an installed plant? Try to exchange the IMs with the other racks and monitor if the error moves with the IM or it is on the same same rack? |
Best Regards |
|
4/19/2016 11:02 PM | |
Posts: 112 Rating:
|
@Khaled_Ezzat Is this error related to any process action? Not really, the error just comes randomly every 10 minutes. Is there any frequency convertor near to the communication cable? No Are you in a commissioning phase? or it is an installed plant? Yes we need to run tests in this new part of the plant if the software works properly, this cannot succeed if it loses connection all the time and I get runtime errors. Try to exchange the IMs with the other racks and monitor if the error moves with the IM or it is on the same same rack? I could change the IM, I will try this tomorrow. |
Last edited by: AGrS at: 4/19/2016 11:06:47 PMLast edited by: AGrS at: 4/20/2016 8:57:59 AM |
|