Dear Sir, I was also getting same error in my PLC with same configuration. But i don't have any analog inputs..Can you help me out from this issue... Regards, Azharuddin ------------------------------------------------------------------------------------------ |
Last edited by: CS Moderator at: 12/31/2018 12:56:09 PMNew subject after splitting |
|
12/31/2018 2:00 PM | |
Joined: 7/7/2010 Last visit: 1/24/2025 Posts: 15558 Rating: (2468)
|
You have 2 analog inputs on the s7-1214 if I recall correctly..... The S7-1200 system manual recommends jumpering all unused voltage analog inputs. Do you have them jumpered so the voltage sensed is always 0V and no floating?
|