3/16/2010 8:44 AM | |
Posts: 7 Rating:
Hi, We are having hot redundant CPU400 . We are trying to communicate ABB system using M-link profibus DP . M-link is configured in 244 read -124 write mode. There is no error in compiling and downloading .But when we take both Mlinks on network the CPU goes to stop mode. I have attached the configuration in PDF .Please let me know if any solution for this. AttachmentMlink_profibus.pdf (182 Downloads) |
3/16/2010 12:37 PM | |
Posts: 24 Rating:
Can you show us your diagnostic buffer? Thanks! |
3/17/2010 4:38 PM | |
Posts: 691 Rating:
Dear sforsameer The Hardware configuration you made for communicating the M-link in Profibus is wrong You should take one Redundant IM ( which supports DP/DP Communication) Have a look at the Attachment |
3/18/2010 11:52 AM | |
Posts: 7 Rating:
Hi chimpu , Thanks for ur reply. I have attached one more configuration . Please let me know if its ok and ifI will be able to achieve them-link redundancy. I have tried with your solution but I am getting errors during compiling. Please let me know if you got any errors. Regards, Sameer AttachmentY-link.pdf (147 Downloads) |
3/21/2010 4:11 PM | |
Posts: 691 Rating:
Dear sforsameer The configuration is OK You have configured 2 M-link in 2 different Racks What error you are getting??? Have you configured I/Os ( Input Output Address) in the M-Links??? |
6/9/2015 1:41 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4770 Rating:
Follow us on