Hello everybody, do you have some experience with DP-DP Coupler (6ES7 158-0AD01-0XA0) connected to IM308C? Could somebody help me? Thanks Vitas |
5/15/2012 2:32 PM | |
Joined: 9/27/2006 Last visit: 10/11/2024 Posts: 12287 Rating: (2685) |
Hello Vitas; What problem do you have exactly? A descrption with some screenshots would be helpful. Normally, with a IM 308C master you should only have to integrate the DP-DP Coupler gsd file (found here: http://support.automation.siemens.com/WW/view/en/113602) in Com Profibus, the Profibus configuration software for the IM 308C, insert a DP-DP coupler as a slave to your IM 308C in the configuratorand configure the data exchange areas properly. What is the second master you are exchanging data with, using the DP-DP coupler? How are the data exchange areas configured there? Note that the data exchange areas on each side of the DP-DP coupler have to be of the same size and datatype, but reversed (an Input area to the slave on the IM 308C must be an Output of the same sixze on the second master....). Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 5/15/2012 4:06 PM |
|
5/23/2012 7:27 PM | |
Posts: 74 Rating: (2) |
Hello IBN-Service, Thank You very much for Your information, now I feel better. Vitas |