4/28/2020 1:18 PM | |
Posts: 4 Rating:
|
Hello Please I need to help I have problem on mag 5000 display , the flow rate appear as ####### ...sent from App |
4/28/2020 3:48 PM | |
Joined: 3/28/2010 Last visit: 10/2/2023 Posts: 978 Rating:
|
Fascinating what's in the Mag 5000 manual. ##### is an indicator that the totalizer has maxed out and needs to be reset. https://i.postimg.cc/CKqSSyN7/pound-sign-error-is-totalizer-overflow-need-to-reset-the-totalizer.jpg |
Last edited by: danw at: 04/28/2020 15:49:06 |
|
This contribution was helpful to
2 thankful Users |
4/28/2020 10:07 PM | |
Posts: 4 Rating:
|
I already reset totalizer but the problem not solved Note/ the totalizer always counts even when there is no flow
...sent from App |
4/28/2020 10:12 PM | |
Joined: 3/28/2010 Last visit: 10/2/2023 Posts: 978 Rating:
|
Mag 5000 has two totalizers. Have you reset both of them? |