12/15/2019 2:46 PM | |
Posts: 1283 Rating: (105) |
|
12/15/2019 2:46 PM | |
Posts: 1283 Rating: (105) |
|
12/15/2019 2:57 PM | |
Joined: 3/28/2010 Last visit: 12/6/2024 Posts: 1095 Rating: (215)
|
1. Mag 5000/6000's are shipped from the factory with the Current Output disabled. You might need to enable (Turn ON) the current output with the pushbutton/display menu or via HART. See my app note (attached) for menu navigation. 2. Have you checked your input with a milliamp source to 'prove' it reads a signal? Attachment01 Siemens Mag 5000-6000 0-4-20mA current output.pdf (711 Downloads) |
Follow us on