Hello Khalid; There is a great amount of information on Siemens automation products available on the forum and on Support pages. You could have easily found the CP 341 RS-232 manuals using the Search box at the right of this page, and I encourage you to do so dilligently. It is not enpough to understand the pinout of the CP, you must match itsignal bysignal to the slave you are connect it to: RS-232 connnections are not much standarddized. In any case your search would have brought you here:
SIMATIC S7-300 CP 341 Point-to-Point Communication, Installation and Parameter Assignment In this manual you would have found the following diagram (in attachment). Hope this helps, Daniel Chartier |
||||||||
4/27/2015 4:04 PM | |
Posts: 81 Rating:
|
Do I need to connect PIN # 1 and PIN # 9 also which are DCD and RI respectively |