8/29/2009 1:51 PM | |
Joined: 10/7/2005 Last visit: 4/26/2025 Posts: 3047 Rating:
|
Hell Kanag's I'll try to clarify: Address 0 is reserved for Profibus configuration/diagnostic tools and you will (should) not be allowed to use thisaddress in your DP Master configuration tool. Adress 126 isthe "default" address for DP Slaves whichsupport address setting via software rather than via DIP switches (typically found in Profibus PA devices, but DP devices can support this too). Address 127 is abroadcast address (used by the DP Master to send for example "clear", "sync" and "freeze"commands which are then evaluted by all Slaves on the bus). This leaves you with adresses1 up to including 125as the "useable" addresses for the Profibus configuration. As you will need at least one DP Master, it also leavesyou witha maximum of 124 DP Slaves. Last but not least, the HSA (Highest Station address) is only of relevance for the DP masters, and is NOT the highest DP Slave address. The HSA determines up to which address the DP Master "scans" the bus to find otherDP Master. I hope this helps |
Cheers |
|
This contribution was helpful to
10 thankful Users |
8/29/2009 3:35 PM | |
Joined: 10/7/2005 Last visit: 4/26/2025 Posts: 3047 Rating:
|
ABB engineer doesn't know what he's talking about (or you misunderstood his "advise")
You have a number of choices Kanag, but they all boil down to usage of a so called Class 2 DP Master (your can not do this from your S7 PLC which is a Class1 DP Master). Siemens PDM (Process Device Manager) is one toolthat can be used for this purpose (and commonly a "fixed" part of the Control system installations when PA devices are used). you can find out more about PDMin thismanual: PDM V6.0 The Process Device Manager manual Alternatively, you can get Profibus troubleshooting tools whichcater for this too (and have the advantage toalways come in handy for Profibus installation verification/troubleshootingon this and other projects). My favourite choice forthis is Procentec's Profitrace(if you opt for this solution make sure to buy the package that includes ProfiCaptain which is the Class 2 capable DP Master, you can find out more aboutthis at www.procentec.com). I hope this helps |
Cheers |
|
This contribution was helpful to
1 thankful Users |
9/3/2009 8:38 AM | |
Joined: 10/7/2005 Last visit: 4/26/2025 Posts: 3047 Rating:
|
Crikey, how could I have possibly NOT been aware of that feature ins Step 7? Thanks Kanag's for finding this and letting us know, it appears that fritz too does sometimes not know what he's talking about |
Cheers |
|
This contribution was helpful to
3 thankful Users |
2/26/2019 2:46 PM | |
Joined: 7/7/2016 Last visit: 7/22/2022 Posts: 5 Rating:
|
Thank you Fritz |
Follow us on