5/2/2011 10:01 AM | |
Joined: 10/7/2005 Last visit: 4/26/2024 Posts: 3004 Rating: (1046)
|
Hello Mushriq if I understand you correctly you only have a handlful of DP Slaves that you want to connect to the CPU, correct? If that's the case (or even if it is a few dozen DP Slaves) I wouldn't worry too much as the CPU can easily handle it. The absolute I/O limits of the 319-3 PN/DPcan be found in the technical spec (see HERE for more) and are: - 8 Kbytes of I/O's address area in general. - 124 DP Slaves per DP Master port (of which your CPU has two and you can add more via CP342-5 if need be). - 244 bytes of cyclic I/O data per DP Slave (this is a Profibus standard value and applies for any DP slave). I hope this helps |
Cheers |
|
5/2/2011 11:06 AM | |
Posts: 947 Rating: (45) |
In additional: Without repeaters you can connect max 32 node (slave). |
Last edited by: gre_m at: 5/2/2011 11:07 AM |
|
3/23/2014 6:00 PM | |
Posts: 17 Rating: (0) |
Dear Sir, What if i need to add more than 32 slave. Thanks and waiting for your reply.
|
3/24/2014 11:49 AM | |
Joined: 1/21/2013 Last visit: 3/19/2024 Posts: 4618 Rating: (705) |
Hello Hazem, Check specification of your CPU if more than 32 slaves. |
3/24/2014 5:47 PM | |
Posts: 17 Rating: (0) |
Dear Sir, Actually i can not find it in the properties in the CPU, could you tell where is it. Thanks & waiting for your reply.
|
3/24/2014 9:06 PM | |
Posts: 17 Rating: (0) |
Dear sir, it is 414 !!
|