Please tell me how are Maximum Expansion module connect to LOGO! BM 12/24 RCE 1P 6ED1052-1MD00-0BA8? |
4/18/2017 6:09 AM | |
Joined: 12/18/2014 Last visit: 1/16/2025 Posts: 34498 Rating: (4306)
|
For the analog inputs, it depends on how many analog inputs you use on the basic module. A LOGO! 0BA8 can manage max. 8 analog inputs. On the basic module 12/24 RCE are 4 analog inputs 0-10V. If you use all 4 analog inputs of the basic module, you can still use 2 expansion modules for analog inputs. For the analog outputs, the LOGO! 0BA8 also manage max. 8. Since there are no analog outputs on a basic module, you can use max. 4 extension modules for analog outputs. AttachmentLOGO! 8 Soft manual 0BA8 2016_07 (FS4) pages 32-34.pdf (652 Downloads) |
4/18/2017 6:14 AM | |
Joined: 2/12/2014 Last visit: 5/28/2023 Posts: 158 Rating: (0) |
Thank you very much |