Hello, Denilson! I'm trying to talk a S7-1200 1214C with Toshiba drives via Modbus TCP through the CLP Profinet port. The Modbus addresses of these inverters are in the extended area. For example, the inverter status word is at address 64770 (FD01h + 1). When I prepare the MB_Client version 3.1 block to read at this address, I get error code 8381 = Function code is not supported, as if the parameters were not interpreted as function 03 = reading holding registers of Modbus. In the same network, with Weg inverters, with addresses within the Modbus low range (40000 to 49999) the same block operates well. Do I have to pass to MB_Client version 4.0 or is it another problem?
------------------------------------------------------------------------------------------ |