2/28/2018 9:39 AM | |
Joined: 4/28/2015 Last visit: 10/9/2023 Posts: 394 Rating: (55)
|
Hello #dP, maybe you have to manipulate the analog output value in OB "MC-PostServo" and to split the analog output value into absolute value and algebraic sign. The handling of the analog output value you could find in system manual, chapter A.10.7. The algebraic sign you send to an digital output of the CPU, connected to the drive. |
2/28/2018 10:42 AM | |
Posts: 2826 Rating: (684) |
Hello. Thank you for your answer and I apologize for not being clear.
How to manipulate the result to the actual analog output is clear to me. This is not the source of my problem. Please see my previous post for a picture. The red encircled entry is a WORD specifically DB3.DBW0. It is this DB3.DBW0 that will be read in OB95 and manipulated to give an analog output. My question: Thanks for your attention. |
2/28/2018 3:18 PM | |
Joined: 4/28/2015 Last visit: 10/9/2023 Posts: 394 Rating: (55)
|
Hello, I think, it is ranged like it is written in system manual in chapter A.10.7. System manual says: I would try to use SCL-command "WORD_TO_INT..." to see the value as an integer value... |
2/28/2018 3:42 PM | |
Posts: 2826 Rating: (684) |
Hello.
There is logic to your suggestion. Possibly huggy_d1 was thinking in the same way. Sincerely. |
Last edited by: #dP at: 2/28/2018 3:45:03 PM |
|