Hi there, your MC_Power instance shows an ErrorID 8001, which states that there is an error at the technology object (TO). See here for information on the ErrorID: https://support.industry.siemens.com/cs/de/en/view/109781853/142655741067 Check the TO's parameter <TO>.ErrorDetail.Number, then check the manual what the error means. This can be found here in the corresponding chapter: https://support.industry.siemens.com/cs/de/en/view/109781853/140294561547 You should also read how MC_Power works, your understanding of Busy and Status is incomplete. Busy only shows that the instruction is working. Status shows if the TO really is enabled then. See here: https://support.industry.siemens.com/cs/ww/en/view/109781849/142862080907 Also it seems you do not check the prerequisites for enabling the TO with MC_Power. Checking these, and only enabling the TO with MC_Power when these are fullfilled, is absolutely mandatory! See here for closer information: https://support.industry.siemens.com/cs/de/en/view/109750297 Implement the checks as shown in the FAQ, then check the behavior again. Regards, |