7/19/2009 8:50 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (309) |
Hello, The MD 741 is modem/router (not only a modem between ethernet and GPRS). It routes packets to the internet like nay other router when the packets are intended for a target in the Internet, but over GPRS (which is a wireless network connected to Internet). You do not send the DBs to the MD741, but to a target system (like another PLC or a PC) connected to the Internet. For the CU315F, the MD 741 is just the default gateway andbehaves just like any other router. Normally the MD741 builts a VPN tunnel, for instance with a Scalance S612. Once the tunnel establisched, it is juts like it doesn't exist for your 315F. In Step7 you configure connections just like the MD740 wouldn't exist (execpeted that you configure the CPU315F to use a router which is the IP address of the MD741 on Ethernet). Example of this kind be found here. http://support.automation.siemens.com/WW/view/en/24960449 |
Last edited by: edr at: 7/19/2009 8:53 PMBest regards |
|
7/19/2009 9:34 PM | |
Joined: 3/21/2006 Last visit: 1/14/2025 Posts: 10239 Rating: (1182) |
Hello, About necesary settings forMD741 modem look at manual - EGPRS/GPRS-Router SINAUT MD741-1 System manual. For the connection with CPU, you need ethernet interface for remote monitoring. Perhaps follow link could be halpful: SINAUT ST7 Configuration in a secured EGPRS Environment with MD741-1/ SCALANCE S612 (Configuration 8) Regards, Hristo Mihalev |