Link to module information: https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&lang=en&objid=6ES73317TF010AB0&caller=view From the technical data, you find Basic accuracy is +/-0.1%, operational (0..60C) accuracy is +/-0.15%. |
5/31/2011 3:33 PM | |
Posts: 510 Rating:
|
Here is a link to the manual that should tell you everything you need to know http://support.automation.siemens.com/WW/view/en/22063748 regards billwest
|