Dear Siemens Project Engineers, would you enlighten me the step of migration OP7/DP to KP400 Comfort? i'm a rookie in migration process the HMI OP7/DP & PLC is 6AV3607-1JC20-0AX1 & 6ES7313-5BE01-0AB0 see the attached picture i have read some OP7, OP17 Operator Panel and download ProSave 10.0.1 some question to enlighten me: - is it posible to transfer the image file using prosave with PC adapter like 6ES7972-0CB20-0XA0 or 6GK1571-0BA00-0AA0 and do i need to buy 6XV1440-2KH32 cable? - is there any safety step to migrate OP7/DP program into KP400comfort? using WinCC(TIA) {thank to IBN-Service} thank for any enlightment Siemens Project Engineers. regards light |
Last edited by: lightbulb at: 3/24/2014 9:33 AMLast edited by: lightbulb at: 3/24/2014 9:18 AM |
|
4/3/2014 8:55 AM | |
Joined: 4/24/2006 Last visit: 2/14/2025 Posts: 8848 Rating:
|
Hello lightbulb, You need the original OP7 Protool project. (No Prosave backup can be used) This protool project can be migrated using WinCC flexible 2008 + SP2 (Do not install SP3, migration is not possible) Have a look at the following manual: SIMATIC HMI WinCC flexible 2008 WinCC flexible 2008 Migration Then you need WinCC Comfort (TIA Portal) to migrate the WinCC flexible project into a WinCC TIA portal project. After that you can change device to KP400 Comfort. Best regards, Wizard |
Last edited by: Wizard at: 4/3/2014 8:55 AM |
|