Hi! For detailed information of configuring failsafe AI-reading, please refer tothismanual. English is not native for me, but if I understood you question correct, you mean monitoring time and in is possible to configure it according with manual: F_monitoring time 0...65535ms Default 2500ms //Monitoring time for failsafe communication between the CPU and the F-AI. You can change monitoring time to desired value with hardware configuration tool. Refer to same manual, page 21. Note: On the Siemens Support website aspreadsheetis available which aids users in calculating failsafe monitiring times. |
Last edited by: olloy at: 5/29/2014 1:33 PMlink corrected |
|
This contribution was helpful to
3 thankful Users |
5/31/2014 10:37 AM | |
Posts: 73 Rating:
|
Hi, You could refer attached excel sheet 'S7 ftime.xls' for better estimation of minimum cycle time of Safety Analog Input. Regards, Krrish !! AttachmentD:\s7ftimeb.zip (210 Downloads) |