11/16/2011 2:00 AM | |
Joined: 10/7/2005 Last visit: 6/6/2023 Posts: 2966 Rating:
|
Hello BeVee yes you can mix P and Q peripherie in one profibus node(see also HERE), so I'm not too sure what's wrong in your case. Things to check would be: 1.) Make sure touse "O" as the address identifier (e.g. L OW 174) in your S5 program for theconfigured "Q area" addresses(do NOT use "Q" in the S5 program as thisnominatesOutputs in the Process Image and this easily causes confusion as "Q" is also incorrectly used in the examples in Appendix B of the ET 200 Distributed I/O System manual). 2.) Make sure to set "Word consistency" for the "Q area"related moduleaddresses in the COM PB config. Should the above not help, pelase upload you COM PB config here and S5 program for evaluation. |
Cheers |
|