11/17/2012 4:28 AM | |
Joined: 9/27/2006 Last visit: 3/20/2025 Posts: 12344 Rating:
|
Hello neni; And welcome to the forum. Based on the information in the Lumel ND1 Modbus manual, the addresses starting at 7000 are equivalent to those at 4000, except that the 4000 addresses are 16-bit, and those iat 7000 are 32-bit.. And 4000 addresses are more standard for Modbus Function 3 operations. See the attached extract from the manual: ND1 Modbus - Lumel I suggest you modify your request to request the 4000 addresses you need, but you must request 2 registers (16-bit) for one of the 7000 values (32-bit floats). Register bytes of sfloat type are sent in 2143 sequence
Hope this helps,
|
This contribution was helpful to
1 thankful Users |