Hello, Are you getting any error from the block when trying to communicate more then 32 words? What is Value of Status Word? Here is the sample Program for Modbus RTU might help you. S7-1200 communication modules -- Configuring and programming communication -- MODBUS RTU |
VANDE MATARAM..... |
|
5/28/2014 1:46 PM | |
Joined: 5/28/2013 Last visit: 2/1/2023 Posts: 112 Rating:
|
Thanks for answering Amit_86, No fault code from the Status Word, i got "0000" |
5/28/2014 2:20 PM | |
Joined: 11/21/2007 Last visit: 3/16/2025 Posts: 2326 Rating:
|
Hello BBPrudente Pl Check the Modbus manual of your slave device. Sometimes the slave devices have a limitation on the max no of registers that they can transmit in one message. I once had an Energy Analyser that could only transmit maximum 20 registers in one message. Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
This contribution was helpful to
1 thankful Users |
5/28/2014 3:18 PM | |
Joined: 5/28/2013 Last visit: 2/1/2023 Posts: 112 Rating:
|
ThanksNavnag for the answer, I will check the device limitation.
|