6/14/2012 1:49 PM | |
Posts: 9 Rating:
|
Dear all, I have a modbus master slave communication problem.!! Please i need your help. for this see attachement please Best regard, Maro AttachmentModbus.PDF (270 Downloads) |
6/14/2012 5:58 PM | |
Posts: 3093 Rating:
|
Hello Maro, I recommend to use presetting of the receiving line of R(A) 0V and R(B) 5V. Regards, Kaulquappe |
6/15/2012 2:53 PM | |
Posts: 9 Rating:
|
Thank you everyone for yours answers, i appreciate it. To Dchartie: My programe at the master side is looking like: (Master) (Dchartie 1): FB7(Modbus control) is called in OB1 as usuallFB7 looking like: see network 3(copy data to be send), network 4 (FC81 send data), network 5(FC82 receive data) and network 6.see attachements please. The status message of the all bloks of master as well of slave: The status is changing from 0 to 7695(16#1E0F) each cycle The error is changing from 0 to 1(each cycle) To Kaulquappe:It doesn’t help .It stil not working guys, very strange.
AttachmentModbus 2.PDF (175 Downloads) |
6/15/2012 3:56 PM | |
Posts: 3093 Rating:
|
Hello Maro, now I got why your receive error 1E0F, you used R_TYP = D but it should be R_TXP = X. And R_NO should be empty. Regards, Kaulquappe |