8/13/2010 6:04 PM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello sun; Here is a quote from GE concerning the communications setup for the PQM meters: The PQM is always a Modbus slave; it cannot be programmed as a Modbus master. |
8/13/2010 6:10 PM | |
Posts: 152 Rating:
|
hello dchartier many thanks for info. now i am sure he is mistaken, thanks cheers sun |