Does your solution relate to USS? I am not sure how that should work. To which register should I send it to? I can't write multiple bytes to one register. If I would do so, I would overwrite the others following registers. Or do you mean, I should write the same command (address, functioncode, register address, value, crc) multiple times. But I am not pretty sure, that's not what you mean. If I send 4000 to setpoint frequency (40003) is changed the register to that, but the VFD does nothing. If I then, read 40003 the frequency is correctly set to 4000. I did do the reset (accord. to link), but the VFD just does not react at all. It seems like I can't control the VFD by changing any register. What I am wondering about, are the STW, HSW, PZD Commands. There is a Register (40100:STW) that is writable and I am not sure if I should write some bit sequence to that register. I tried 0xFFFF, but and 072 Error occurred immediately. My first understanding was to write 40004 (RUN ENABLE) to 1, then 40007 (Fault acknowledgement) to 0/1 (tried both) and then start the motor with 40006 (CMD Start) with 1. I can read out the registers and they did change, but the motor just does not react at all. The display shows 0.00 (not blinking) all the time. By the way, Parameter P1070 (Main Setpoint Source is not a Register - can't write to that via Modbus RTU) is set to 2018.1 and I have a clue what that means and there is no sufficient explanation to that in the manual.
|