Hello dolby; First, there are a few free downloadable Modbus master simulator programs on the web. We used Modscan32 for our Modus tests: Download ModScan32. - WinTECH Software This guide could be useful: Modscan32 Quick Start Guide for ModBus or Johnson Controls N2 https://support.industry.siemens.com/cs/ww/en/view/23907920 Now, as far as connections on the Com port (very probably RS-232C), you should find out what model of CP 341 you have in hand. There are RS-232 (6ES7 341-1AH02-0AE0) and RS-485 models (6ES7341-1CH01-0AE0). If the CP 341 has a RS-232 interface 9same as your COM port), you only need to check the pinout for the module and build a cable that connects with the right COM port pins. If it is a RS-485 communication module you need a converter from RS-232 to RS-485 (there is a large number of manufacturers that can be found on the web), then use a proper cable between the converter and the CP 341. You will probably have to go to an electronics shop to purchase a 15-pin Sub-D connector to build the cable for this interface. See Appendix B of this manual for the pinouts for different models of CP 341. SIMATIC S7-300 CP 341 Point-to-Point Communication, Installation and Parameter Assignment https://support.industry.siemens.com/cs/ww/en/view/1117397
Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 2/21/2016 9:02:27 PM |
|
This contribution was helpful to
3 thankful Users |
2/23/2016 7:49 PM | |
Posts: 3093 Rating:
|
Hello Dolbyinside, The master should read from address 0 and write to 1536. Regards, |