7/28/2016 8:03 PM | |
Joined: 3/28/2010 Last visit: 3/13/2025 Posts: 1123 Rating:
|
1) Lack of Fail-safe biasing A periodic fault (every so many hours/days) like this can occur if there is no RS-485 failsafe biasing. I don't know if Siemens modules are fail-safe biased or not, because I'm a Modbus guy, not a Siemens guy. The section on fail-safe biasing on pages 8 and 9 of the National Semiconductor AN-1057 app note, "10 Ways to Bullet Proof RS-485 Interfaces" has a decent explanation. Google or download it here: 10 Ways to Bullet Proof RS-485 Interfaces
Intermittent ground loops, if beyond the common mode limits of the RS-485 drivers can saturate the drivers and fault the 485 network. The practical solution is to put an RS-485 isolator in the network, as opposed to trying to find the source of the common mode and trying to eliminate it. I have had to put in two isolators on multidrop networks, one at the master, another half way down the network, in order to eliminate enough common mode to keep the network running. 3) Multiple slaves, one slave's driver is flakey A slave's driver that fails active can lockup the entire network. Sometimes cycling power will restore the slave's driver temporarily, but eventually it fails. The effort is in finding which slave has the bad driver. Logs showing faults like time-outs can be used to see who was the last slave before the time-out happened. |
This contribution was helpful to
1 thankful Users |