Dear Expert, I have following configuration : PLC : S7-1500 CPU-1511 RIO : ET200SP CM : ET200SP CM Ptp Modbus Network : 5 Protection Relay + 5 Power Meter Accuvim-L ( modbus ID : 1-10 ) Port configuration (CM Ptp, Protection Relay, Power Meter ) Baud : 19200 Parity : None Data bit : 8 Stop bit : 2 I have verified there's no wiring error for DT(A) and DT(B) cable. I can't retrieve data from protection relay, everytime it give me error #80C8 (there's no problem with power meter) using pc software modbus scanner over usb-rs485 converter to 7sr12 : OK If i compare the command from pc software (modbus scanner) and CM ptp command, there's no different, except for the last 2 byte (crc check byte ). On CM Ptp there's no crc check byte. I already check CM Ptp send buffer when i read power meter(successfull read), it's the same there's no crc check byte on the send-buffer. I think crc byte on CM ptp was handle on the other place. attached are picture : modbus scanner.png (screen shoot of pc software modbus scanner ) cm-ptp send buffer.png (screen shoot CM Ptp send buffer ) cm-ptp receive buffer.png (scrren shoot CM Ptp receive buffer, related with send buffer) Please help Rusli