Hello, Check the outputs of the Modbus FBs in your program and tell us the result. How do you evaluate the status of system blocks in STEP 7 (TIA Portal)? Regards, |
6/16/2019 8:08 AM | |
Joined: 11/3/2016 Last visit: 6/11/2023 Posts: 3 Rating:
|
I looked at the error status. This is error 8180. Made an update of the operating system firmware for version 4.02.03. I do not know why, but modbus RTU began to work. |