10/6/2020 10:46 AM | |
Joined: 3/30/2020 Last visit: 1/27/2023 Posts: 3036 Rating:
|
Hello. What is the link between the PT100 PT1000 sensors and Modbus RTU? Any specific reason that you are not wanting to use the |
Last edited by: qwazee at: 10/06/2020 10:48:34Last edited by: qwazee at: 10/06/2020 12:16:50Typing error PT100 -> PT1000 |
|
10/6/2020 11:45 AM | |
Posts: 17 Rating:
|
Maybe the title was a little bit misleading. The reason I don't use the module is simple. Snapping the CM on the PLC is easy, but communication via modbus is something more challenging for me. The company I work with uses PT1000 sensors wired to a Aucxis cards which is further wired on the PLC, but since they are custom made there is absolutely no info on them as to what kind and/or where to find them and have some starting refference in this field. What can I you suggest as a link from the PLC to the sensors? Thanks. |
10/6/2020 12:19 PM | |
Joined: 3/30/2020 Last visit: 1/27/2023 Posts: 3036 Rating:
|
Did you follow the link I have left you in my previous reply? Attached is some more information of a card that can make the PLC read the PT1000. AttachmentRTD-add-on.pdf (47 Downloads) |