6/22/2016 3:23 PM | |
Joined: 1/30/2006 Last visit: 3/17/2025 Posts: 310 Rating:
|
There is a FAQ talking about Multiport. In Genral your CPU must be FW4.1 or higher to support Multiport The maximum number of Modbus clients that can be connected to one S7-1500 CPU is determined by the number of MB server FB instances running in parallel on the CPU and the maximum number of free connection resources. https://support.industry.siemens.com/cs/us/en/view/34010717 |
BR. Sven |
|
6/22/2016 3:24 PM | |
Posts: 439 Rating:
|
Hello, Which ports are released for Modbus/TCP communication and how many Modbus clients can communicate with a SIMATIC S7 CPU as Modbus server?You can have multiple Modbus connections if you use a different port for each MB_SERVER instruction. The CPU you are using will restrict you on the maximum number of connection and the port you need to use. I did the test on a previous project and you can use port 502, 503 and 504 to communicate with 3 modbus client at the same time. I hope this will help you. Best regards, Hugo |
6/23/2016 1:20 PM | |
Joined: 5/11/2010 Last visit: 3/7/2025 Posts: 90 Rating:
|
Hello friend, note: wincc v7.0 will communicate with s71200 via opc only. you need to check the possibility of using opc and modbus tcp in same port.
|