Dear Praveen Patil, You have the right module, connect it as a RS485 module to the master, please look very well if the wiring is ok.. In the handbook Serial Interface Module ET 200S 1SIyou will find how to program the MODBUS Slave in chapter 3.6 as of page 3-55, The Function Codes 01, 02, 03, 04, 05, 06, 07, 08, 11, 12, 15 and 16 may used. There is like FB80 for the CP341 also a FB81 "S_MODB" that have to be used for the best programming, seeFunction Blocks, Examples and User Manuals for the ET200S 1SI Serial Interface for the blocks and a example. |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|