Hi, for holding register you have to use data_type = 3 and for input register you have to use data_type = 4. For modbusTCP communication you can't use the TCP wizard, the "ModbusTCP wizard" is the correct wizard. The manual with a Getting Started you can find here: OpenModbusTCP, tab "Downloads". After installation you can also find example projects (search with "Browse" button in SIMATIC Manager). Wüstenräuber |