Posts: 3093 Rating:
|
Hello, Regards, Now I'm really confused, there are three Unit IDs mentioned in the Schneider manual: 0, 251, 255. I can't understand when to use which one. |
Last edited by: Kaulquappe at: 9/5/2018 1:55:22 PMLast edited by: Kaulquappe at: 9/5/2018 1:59:13 PMLast edited by: Kaulquappe at: 9/5/2018 2:04:16 PMLast edited by: Kaulquappe at: 9/5/2018 2:05:27 PM |
|
9/5/2018 2:04 PM | |
Posts: 10 Rating:
|
sorry, i could not get your question.. could you please brief it..it is modbus tcp communication |
This contribution was helpful to
1 thankful Users |
9/5/2018 2:08 PM | |
Posts: 3093 Rating:
|
Hello, The Unit ID is parameterized in the MB_Client instance DB variable MB_Unit_ID. Regards, |
9/5/2018 2:16 PM | |
Posts: 10 Rating:
|
thank you so much for your timely help... |