11/28/2014 6:28 AM | |
Posts: 40 Rating:
|
Hello All, I think i spent too much time in modbus Communication.Yet to get clear solution But if laview is configured as client (same parameters configured in plc MB_CLIENT) and 3rd party device as server, modbus communication establishes . The same 3rd party device connects with a application MODSCAN ,Modbus communication establishes. Here am listing the parameter configuration . My plc Ip address: 192.168.1.2 Port Id : 502 LABVIEW IP :192.168.1.60 port id :502 3rd party device IP:192.168.1.7 port id : 502 I am attaching Some images and My program for your reference (TIA v11 sp2).Please guide me. Regards prasanna thanks in advance AttachmentModbus tcp PLC asCLIENT.zip (131 Downloads) |
11/28/2014 6:32 AM | |
Posts: 40 Rating:
|
Hello Am attaching Some images for your references . Regards prasanna G.K
AttachmentImages.zip (78 Downloads) |
12/2/2014 5:23 AM | |
Posts: 40 Rating:
|
HelloKaulquappe, Thank you sir.Finally am able to communicate my plc with 3rd party device .I changed MB_UNIT ID in MB_CLIENT PARAMETER .Finally it works Regards Prasanna Gk
|