4/28/2016 7:55 AM | |
Joined: 10/3/2008 Last visit: 8/28/2024 Posts: 961 Rating: (124)
|
Hi, the reason is the PAC3200. This PAC can establish only 1 connection on port 502, so the H-CPU can only establish 1 connection. The try to establish the second connection is rejected by the PAC. PAC3200/4200 - Support of Ethernet Modbus TCP communication connections If you would use PAC4200, both connections can be established.
|
Last edited by: Wüstenräuber at: 4/28/2016 7:57:25 AM |
|
4/28/2016 10:48 AM | |
Joined: 10/3/2008 Last visit: 8/28/2024 Posts: 961 Rating: (124)
|
Oh... Thanks, Kaulquappe! Wüstenräuber |
4/28/2016 7:17 PM | |
Posts: 30 Rating: (1) |
@Wüstenräuber Understood. Thanks for your support. @Kaulquappe Appreciate for the information. |