Hello s_vb you can use the PN port of the CPU for UDP (or TCP andISO on TCP) but it will NOT be configured in NetPro. Instead you use so called "Open Communication" which means the connection is configured, established and used via your user program and below are a few links with more on this: How do you program the communication blocks FB67 "TUSEND", FB68 "TURCV", FB65 "TCON" and FB66 "TDISCON" in order to use the UDP protocol for data exchange by means of the integrated PROFINET interface of a CPU? Wizard for creating connection data for open TCP, ISO on TCP or UDPcommunication (Open Communication Wizard). I hope this helps and good luck with your "Modbus on UDP" implementation. |