11/3/2015 6:43 AM | |
Posts: 8 Rating:
|
Good day excellence, I'm trying to achieve the communication between S7-1200 PLC V4 / CM1241(RS485) and the Delta Temparature control , but so far there is NO success . The Error that i'm getting is 8383 which really confuse me because I've checked my DATA PTR and it's looks okay , i'm reading 0..5 words and the DATA LEN is 12 bytes which i think is fine . May i ask you guys to assist me please. Thanks
AttachmentModbusrtu_mode.pdf (630 Downloads) |
11/9/2015 4:57 PM | |
Posts: 3093 Rating:
|
Hello, Address 4096 is a coil address. One coil is one bit. When you use DATA_LEN=12, you try to read 12 bit. Regards, |
This contribution was helpful to
1 thankful Users |
3/10/2016 7:57 PM | |
Posts: 3093 Rating:
|
Hello, Regards, |
3/13/2016 11:31 AM | |
Posts: 8 Rating:
|
Good day Kaulquappe I have came right now , see attached short summary of what i did . Siemens Modbus RTU when you connecting with Delta 1000H = 4096 Dec + 400001 = 44097 First holding register if you want to read PV . Thanks it's been very interesting . Regards Soh AttachmentSummary Modbus_rtu with Delta_Temp_Controller.docx (656 Downloads) |
This contribution was helpful to
2 thankful Users |