Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi, when someone asks for a exact module, he normally wants to know the order-no./MLFB But I don´t need it anymore, because of there is only one AQ4-module in ET200MP-Series. All parameters are changeable in Run, over WRREC, using data record 128. The parameters set in STEP 7 are not changed in the CPU, which means that the parameters set in STEP 7 will be valid again after a restart. you can read this information in the manual of the module: SIMATIC ET 200MP Manual Collection page 2670 and 2496. AI module parameters are changable too hope this helps, regards, |
Last edited by: mopS04 at: 5/25/2016 11:11:33 AMFCK WAR! |
|
This contribution was helpful to1 thankful Users |
5/25/2016 4:12 PM | |
Posts: 11 Rating: (0) |
I have another question about that block, Do you know if it works when using PLCSIM? I would like to check if it's ok before going on the field |