10/30/2017 7:23 AM | |
Posts: 167 Rating: (1) |
Please see attached diagnostic buffer log file. 64 of 519; Event ID: 16# 08:0100 AttachmentDiagnostics.txt (534 Downloads) |
10/30/2017 8:41 AM | |
Joined: 11/29/2011 Last visit: 4/24/2024 Posts: 1354 Rating: (229) |
Hi, See the SIMATIC S7-1500/ET 200MP Manual Collection under chapter "6.3 Diagnostic alarms" on the page 4053.Search for "Module is defective". It says: "Possible causes: The noise as reason for me make sense due to the random occurrence of the event. Anyways have a think about it and draw your own conclusion. I hope I could help! |
Last edited by: MicroMan at: 10/30/2017 2:44:48 PM- What you read here, please check with manuals and your requirements. |
|
10/30/2017 12:58 PM | |
Posts: 167 Rating: (1) |
Hi, Is it based on Event ID: 16# 08:0100 you make these reference to these document? |
10/30/2017 3:43 PM | |
Joined: 11/29/2011 Last visit: 4/24/2024 Posts: 1354 Rating: (229) |
Hi, Based on the Diag buffer. The F-IOs were passivated but not reintegrated. The power cycle reinitialized your safety program. Again there is a lot into that, I suggest you see the Safety: Passivation and Reintegration of F-I/O Noise. That is a wild guess, I do not see the installation. Noise can get into the panel via galvanic connection as well. Also can be caused by many things inside your panel. That is a wide topic I suggest to open up this discussion in the Communication/Networks conference. That conversation can go very far. |
- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to1 thankful Users |
1/12/2022 12:08 PM | |
Joined: 9/8/2017 Last visit: 4/26/2024 Posts: 4 Rating: (0) |
Hi What is the latest status of your system? are you still getting an error? |