Hello I use 1212C DC/DC/DC CPU ver 3.0.1 firmware mc power error code is16#8612,16#000D and what solve this problem ?
|
9/2/2013 3:20 PM | |
Joined: 8/31/2005 Last visit: 3/24/2025 Posts: 2198 Rating:
|
The picture shows a configuration error. And the System Manual says: 8612: Invalid address of the homing switch https://www.automation.siemens.com/mdm/default.aspx?DocVersionId=56499189643&Language=en-US&TopicId=41514452619 |
|
|