Hello Karnan, It is very likely the variable speed drive controller is attempting to protect motor by estimating the temperature via calculation by motor model. Depending upon your situation, you may want to deactivate this function. Per attachment, you may be able to deactivate this function by setting P0621 = 0. Best Regards, Deputy AttachmentD:\Users\summrl\FY14\Reference\Forum\Motor Temperature Calculate\Motor Temperature Calculate.JPG (413 Downloads) |
4/20/2014 10:36 PM | |
Joined: 5/22/2012 Last visit: 3/24/2022 Posts: 895 Rating:
|
Hello, check function diagramm 8017 + 8016: http://support.automation.siemens.com/WW/view/en/59750648 Especially motor weightp344 is a important parameter Regards Zako |
Last edited by: GrasserF at: 4/22/2014 9:59 AMlink edit |
|