2/6/2016 5:15 PM | |
Posts: 5225 Rating: (1198)
|
The original example can be found: You can still use the method you did before and have the HMI scale to what you need. In this case just remember that the analog value is between 0 and 27648in the raw input. For more information use the search terms SCALE_X and NORM_X. w |
2/7/2016 4:05 AM | |
Joined: 7/29/2014 Last visit: 12/24/2024 Posts: 82 Rating: (0) |
Thanks for the answer and help, but I cannot open the example within that thread (I am using V13). Could you please show an example? |