Hello, I got a problem with a MP270. The MP c'ant read the CF card after 2 or 3 hours of runnig. (even with the windows CE explorator). And some times, the images used in the Wincc application seems to disappear (small cacti replace the images). I changed the panel and the CF Card bye a new and the problem persist. The same type of MP with the same application is used on a other site and the panel works well. If someone has already met this problem... |
5/16/2006 3:45 PM | |
Joined: 4/24/2006 Last visit: 3/13/2025 Posts: 8893 Rating:
|
Hello, Is the CF-cardnew? Have you tried to change the CF-card with one that's working good. (the other application). Greetings, Wizard |
5/16/2006 3:56 PM | |
Joined: 4/6/2006 Last visit: 2/5/2024 Posts: 604 Rating:
|
Dear Auto_Soreel, I guess that you are using WinCC Flexible 2005 without a Service Pack. I would suggest to run the update to SP1 and run a OS Update. And after that you need to download your configuration again. The update is available for download at: http://support.automation.siemens.com/WW/view/en/23059737 Best regards, INS |