Hello Stavros; Depending on the amount of data (it must be small, around54 bytes per GD package for S7-400 CPUs) you could do this with Global Data exchanges over MPI. If not you will have to program S7 function (communication blocks) such as USEND/URCV (less than 200 bytes), or BSend/BRCV for larger volumes of data. To access Global data, open Netpro, click on the MPI network linking the PLCs, and right-click: Define Global Data selection. L:ook for details in Step 7 Online Help, ad in the following FAQ: http://support.automation.siemens.com/WW/view/en/430498 Hope this helps, Daniel Chartier |
6/5/2008 11:10 AM | |
Posts: 52 Rating: (4) |
Thanks for the immediate answer The link was very helpfull |