12/18/2014 2:10 AM | |
Joined: 9/27/2006 Last visit: 4/29/2025 Posts: 12347 Rating:
|
Hello Ajay; Unfortunately, you cannot use OLMs with MPI protocol. See the following FAQ: Setting up an MPI network with PROFIBUS OLMs You would need to use Profibus-DP instead. Hope this helps, Daniel Chartier |
12/18/2014 9:40 AM | |
Joined: 8/25/2006 Last visit: 4/28/2025 Posts: 2214 Rating:
|
Hello. Several years ago I made similiar configuration after consulting with Siemens. There was MPI optical ring consisting of 3 OLM-G12 V3 (6GK1502-3CB10). PLC was Simatic TDC (CP50M0), which was conected via MPI optical ring to 2 PC-station (CP5611) with HMI Protool-RT. That configuration works fine. There was also Profibus optical ring based on the same type of OLM's. The only difference in configuration of OLM's between MPI and Profibus rings was DIL switch S7 in ON position for MPI. So I'm not sure will your configuration work or not, but if you have OLM's you can test this.
|