Hello jabbi_king; The CP 341 provides serial, point-to-point connections over variou physical supports, Rs 232, TTY (curent loop) or RS 422/485. But that does not equate to a supported protocol. Sorry if you heard this from me before, but compare this to a telephone conversation. If I can dial your number and connect to you, it means we share the same physical support layer, wired or wireless. But if you speak English and I only speak French, our protocols are different and our conversation will be pointless, we will not be able to exchange information. So in your investigation you must insure not only that both partners share a RS 485 layer, but that the same protocol and corresponding protocol parameters are setup so both participants can undertand each other. The screenshot below shows the integrated protocols that can be used on a CP 341 RS 422/485 module. For a RS 485 setup, only ASCII protocol is avaliable (as integrated prtocol supported by RS 485). Now have a look at this document showing the different parameters that must be set for ASCII comms: https://support.industry.siemens.com/cs/ww/en/view/1117397/30259101835 Most important to you (as per your last comment) is the character delay time, related to the data speed setup in the driver. You could try all shown speed values in your system, and find the setup speed in your configurtion, maybe. That is if it is an ASCII protocol setup... The CP 341 also allows a Modbus RTU loadable driver to be instaled and configured (after purchase), so the information given for the ASCII confguration would not be useful The way to ensure yourself about the presence of this Modbus driver is to verify is the CP 341 has a dongle installed on the back (the dongle enables Modbus RTU functions on the CP 341): remove the CP 341 from the S7-300 rack, and examine the back of te module; if you find a back plastic rectang;le inserted there, as shown in the following link, then your module is probably using Modbus RTU... https://programmersought.com/article/42043751258/ Hope this helps, |
Last edited by: dchartier at: 06/26/2021 20:34:07 |
|
6/27/2021 2:19 AM | |
Joined: 1/26/2014 Last visit: 8/16/2025 Posts: 164 Rating:
|
Dear its mean on the other side it used EM277. same like CP341? EM277 order no. 6ES7277-0AA22-0XA0 |
6/27/2021 7:20 AM | |
Joined: 4/28/2015 Last visit: 4/19/2025 Posts: 10876 Rating:
|
Hello,
again pls, check my links and compare 2 modules parameters to be sure about functionality: CP341 S7-300 RS422/485 serial module Info EM277 S7-200 Profibus DP Slave module These 2 modules have only physical interface same, other parameters and product functionality points to different tasks. |
With best regards... |
|