3/8/2012 1:18 PM | |
Posts: 1547 Rating:
|
Hello, with PROFINET normaly you have controller - device communication. A device is regular assigned to one controller. Why do you not use the open TCP Communicaiton using the PN interface of the CPU's? Wizard for creating connection data for open TCP/IP communication (Open Communication Wizard). With this configuration you can handle up to 8 connections simultaneous. |
3/9/2012 7:23 AM | |
Joined: 10/7/2005 Last visit: 3/20/2025 Posts: 3042 Rating:
|
Hello GreyEye I'm afraid to say that the 319F-3 PN/DP has a limit of a maximum of 2 I/O Controllers when used as a Shared Device,which perfectly explains what youalready observed (this value is listed in the PROFINET IO Device section of the technical spec of the6ES7318-3FL01-0AB0). |
Cheers |
|