Hello yaray; You can use PUT/GET functions between the S7-400 and S7-300 over Profibus, if you program them in the S7-400 CPU. The S7-300 integrated DP interface can only act as a server for S7 Communicatioons; to act as a client it requires a CP 342-5 in the rack. This is explained in the following documents: Which types of connection/protocols do the S7-300/400 CPUs and the CPs support by default? https://support.industry.siemens.com/cs/ww/en/view/24352751 “S7 300: Client functionality only via CP342-5 from FW V5.2» CPU-CPU Coimmunication with S7 Controllers. https://support.industry.siemens.com/cs/de/en/view/78028908 The screenshots below are extracted from this last document (known as "The Kompendium"). |