1/9/2012 12:49 PM | |
Joined: 9/28/2005 Last visit: 3/15/2025 Posts: 2957 Rating:
|
Hello, Good question. Well accordint to this data http://support.automation.siemens.com/WW/view/en/42982507/tdyou should be able to gave 4 stations communicating with S7 protocol and in total you can have 8 stations with this CP. It would be interesting to see online data about used communication resources. You can do that with MPI. I would like to hear some explanation also from other members. |
Best regards, |
|
1/9/2012 1:08 PM | |
Posts: 66 Rating:
|
Hello Darius, What do you mean with You can do that with MPI ? Thank you. J. Timmermans |
1/9/2012 8:21 PM | |
Posts: 66 Rating:
|
Good idea. Tomorrow morning I will check this Yours, Jtimmermans
|
1/10/2012 10:36 AM | |
Posts: 66 Rating:
|
Hello, Please read the attachement with some printscreens. Maybe it has something to do with the reserved connections? thank you. Yours, J Timmermans
Attachmentconnections.pdf (181 Downloads) |
Last edited by: timmermans at: 1/10/2012 1:20 PM |
|
1/10/2012 11:01 AM | |
Posts: 66 Rating:
|
It looks like the connections. 5x The manual says more connection should be possible Can this be increased?
Yours. J. Timmermans Attachmentconnections2.pdf (155 Downloads) |
1/10/2012 1:05 PM | |
Joined: 9/28/2005 Last visit: 3/15/2025 Posts: 2957 Rating:
|
Try to set reserved OP connections to 5 in HW config for PLC. |
Best regards, |
|