10/18/2016 9:59 AM | |
Joined: 12/13/2012 Last visit: 10/5/2023 Posts: 124 Rating: (45)
|
Hello , you can use PDM for the connection / communication. Simatic PDM 9.x single point for the communication ==> 6ES7658-3HA58-0YA5 Modbus Cable for the connection ==> 7ML1830-1MC Here you will find a guide ( made for PDM 6.x which is similar to 9.x) ==> http://www.automation.siemens.com/w1/efiles/feldg/files/application_guides/en/ag041125.pdf Also this blog is interesting: Hope this helps ! |
This contribution was helpful to1 thankful Users |
11/16/2016 7:01 PM | |
Posts: 32 Rating: (2) |
Thanks! What is the infared link 7ML1830-1MM? Would it allow PDM usage through the infared port, instead of opening the box to connect to the RJ connector?
|
Last edited by: cncsparky at: 11/17/2016 4:45:07 PM |
|
2/22/2017 9:14 PM | |
Posts: 32 Rating: (2) |
Modbus Cable for the connection ==> 7ML1830-1MC Is there an alternative to the Siemens cable? Cost on this one is around $1000 !! The PDM was less than $100. |
2/23/2017 11:44 AM | |
Joined: 12/13/2012 Last visit: 10/5/2023 Posts: 124 Rating: (45)
|
I have double checked this.The listprice of 7ML1830-1MC will be around 70 $. Who gave you a price of 1000 $ ??? |